Posted By: Frank Cinker Storage shed receptacle - 06/02/02 11:54 AM
I believe it would be Code compliant to run one underground branch circuit to a storage shed and install a duplex receptacle without driving a ground rod etc. The single branch circuit would of course include an equipment grounding conductor. Am I correct?
Posted By: golf junkie Re: Storage shed receptacle - 06/02/02 02:07 PM
yes
Posted By: resqcapt19 Re: Storage shed receptacle - 06/02/02 04:21 PM
Frank,
Don't forget that 225.31 requires a disconnect at the shed. The exception to 225.38 permits the use of a "snap" switch as the disconnect.
Don
Posted By: Frank Cinker Re: Storage shed receptacle - 06/02/02 11:02 PM
Thank you for replies. I wasn't aware of the disconnect rule Don. A snap switch is certainly easy enough.