#10222 06/02/02 07:54 AM
F
I believe it would be Code compliant to run one underground branch circuit to a storage shed and install a duplex receptacle without driving a ground rod etc. The single branch circuit would of course include an equipment grounding conductor. Am I correct?
#10223 06/02/02 10:07 AM
yes
#10224 06/02/02 12:21 PM
Frank,
Don't forget that 225.31 requires a disconnect at the shed. The exception to 225.38 permits the use of a "snap" switch as the disconnect.
Don
#10225 06/02/02 07:02 PM
F
Thank you for replies. I wasn't aware of the disconnect rule Don. A snap switch is certainly easy enough.