ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 504 guests, and 20 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
#99452 11/06/05 11:39 AM
Joined: May 2002
Posts: 1,716
R
Member
Paul, as Dmattox points out, they are two different conductors performing entirely different functions.

Read part III of article 250 for GEC; and parts V, VI, and VII for EGC.

Roger

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#99453 11/08/05 04:25 PM
Joined: Aug 2003
Posts: 64
E
Member
Quote
GEC is for connecting your grounding electrodes together to form your grounding electrode system.

dmattox,

Don't mean to be nit picky, but I have seen some get confused by this point. The GEC is used to connect the grounding electrode system to the service grounded conductor and/or equipment grounding conductor (see the definition in article 100). The conductor(s) used to connect the grounding electrodes together are bonding jumpers (See 250.53(C))

Edit: because I realized that by oversimplifying I had introduced some inaccuracies in my post.

[This message has been edited by eprice (edited 11-08-2005).]

#99454 11/13/05 02:01 PM
Joined: Jun 2003
Posts: 681
P
Member
Protection is a dicy subject. Now how do we decipher between "subject to physical damage" and "severe physical damage" when there is no definition of either.

I think it is a great move on the part of the CMP.


Pierre Belarge
#99455 12/04/05 01:05 AM
Joined: Jul 2002
Posts: 717
M
Member
I have never seen a damaged gec in my travels. Has anybody here ever seen one? (not including the #12 one the phone company bonds the demark with). Maybe another bone thrown to the metal conduit boys.