Safety at heights?
0 members (), 516 guests, and 17 robots.
#98314 05/26/06 06:48 PM
Can you install threadless compression fittings underground for a RMC installation?
George Little
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#98315 05/26/06 07:31 PM
Why not? I've done it before.
Checkout article 344.10 (B) Corrosive Enviroments.
#98316 05/26/06 07:32 PM
and 344.42 (A)
#98317 05/27/06 08:07 AM
My thinking is - Just because it listed as suitable for a wet location or corrosive environment does not make it suitable for direct burial.
George Little
#98318 05/27/06 08:17 AM
334.10(B) Corrosion Environments. RMC, elbows, couplings, and fittings shall be permitted to be installed in concrete, in direct contact with the earth, or in areas subject to severe corrosive influences where protected by corrosion protection and judged suitable for the condition.
Is direct burial 'not in direct contact with the earth'?
If not where is the permission to run any RMC or fittings underground?
Bob
#98319 05/27/06 10:36 AM
You got me Bob. Thanks- one of those mental block thngs I guess [Linked Image]
You got your numbers mixed up but I found it.
[This message has been edited by George Little (edited 05-27-2006).]
George Little