Posted By: George Little Fittings Underground - 05/26/06 10:48 PM
Can you install threadless compression fittings underground for a RMC installation?
Posted By: ShockMe77 Re: Fittings Underground - 05/26/06 11:31 PM
Why not? I've done it before.

Checkout article 344.10 (B) Corrosive Enviroments.
Posted By: ShockMe77 Re: Fittings Underground - 05/26/06 11:32 PM
...

and 344.42 (A)
Posted By: George Little Re: Fittings Underground - 05/27/06 12:07 PM
My thinking is - Just because it listed as suitable for a wet location or corrosive environment does not make it suitable for direct burial.
Posted By: iwire Re: Fittings Underground - 05/27/06 12:17 PM
Quote
334.10(B) Corrosion Environments. RMC, elbows, couplings, and fittings shall be permitted to be installed in concrete, in direct contact with the earth, or in areas subject to severe corrosive influences where protected by corrosion protection and judged suitable for the condition.

Is direct burial 'not in direct contact with the earth'?

If not where is the permission to run any RMC or fittings underground?

Bob
Posted By: George Little Re: Fittings Underground - 05/27/06 02:36 PM
You got me Bob. Thanks- one of those mental block thngs I guess [Linked Image]

You got your numbers mixed up but I found it.