XtheEdgeX,
C'mon. You're just picking apart my reply now. Of course the panel is a wireway for the OCPD's. But not for wiring to go through the panel to get to another.
I am picking apart your reply because it is in conflict with the published statements of CMP 9. The code making panel clearly intends that you can use the panel wireway for external conductors. If it is a wireway for the panel conductors, it is a wireway for all condcutors up to the fill requirements in the code section.
I think we just have a few here trying to defend this because they do this.
No, I don't do this, but it is permitted by the code.
I also think it's pretty lousy workmanship to pull wire through a panel like it's a junction box, and to splice wire in panels, instead of laying the job out correctly to avoid this.
I agree that it is poor workmanship, but again, it is code complaint.