ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 520 guests, and 23 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#96825 12/31/05 10:45 AM
Joined: Jul 2002
Posts: 103
J
jes Offline OP
Member
Does anyone live in a jurisdiction where metal soil pipe (DWV) is considered part of the 'metal water piping system' and is therefore required to be bonded? Does anyone do this as a matter of course? What are the criteria to select the bonding jumper and do you connect together sections that may be separated by plastic?
How about using it as a grounding electrode if it exits the house underground?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jan 2003
Posts: 4,391
I
Moderator
Personally I would not call what is in that pipe 'water'.

Quote
250.52 Grounding Electrodes.
(A) Electrodes Permitted for Grounding.
(1) Metal Underground Water Pipe.


Quote
250.104(B) Other Metal Piping. Where installed in or attached to a building or structure, metal piping system(s), including gas piping, that may become energized shall be bonded.....

Do you think the waste pipe may become energized?

I think that would take very unusual circumstances.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Jan 2005
Posts: 5,445
Likes: 3
Cat Servant
Member
I suppose that bonding the drain pipe isn't a bad idea. This would even be desireable in the case of a sump pump, or a 'pump-up' toilet, or other electrical equipment being present that uses the drain line.
In that case, I would prefer to make my bond at the equipment, rather than to a main line. Even cast iron pipe is assembled in a manner that may provide a poor connection between separate pieces. So let's put the electric "drain" near where the electric "leak" is likely to be!


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5