ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 518 guests, and 24 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#96522 12/05/05 05:03 PM
Joined: Jan 2004
Posts: 1,507
G
Member
If I have a 1000a bus bar service - What size GEC do I need to a qualifying water pipe electrode?


George Little
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#96523 12/05/05 05:16 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Assuming that the calculated load is 1000 amps I would say 3/0 CU

See note 2 to Table 250.66

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#96524 12/13/05 08:20 AM
Joined: May 2004
Posts: 162
C
Member
This may be a little late but you might consider that the intent of 250.66 is to provide a grounding electrode conductor that has a cir mil area based upon the cma of the supply conductors. In the case described the busbar would be considered the service entrance conductors???


The conversion from area in mils sq to cir mil area is Amil sq divided by .7854.

A 1/4" X 2" bar would have a sq in area in mils of 250 X 2000 or 500,000 sq mils.

divide 500,000 by .7854 to obtain 636,618 + or - cir mil area.

reference to 250.66 and select a 2/0 CU or a 3/0 Al GEC .

Although one could consider busbar as not fulfilling the intent of the term conductor it is conducting material.

just a thought!

#96525 12/13/05 09:34 AM
Joined: Jan 2004
Posts: 1,507
G
Member
There's a question in my mind about what size buss bar is used for a 1000a. Service. I was under the impression that a buss bar .25" x 4" would be used. Using cpal's math the required GEC would be 3/0 cu. or 250 kcmil al.

250 x 4000 =1000000 sq. mils. 1000000/.7854 = 1273236 cir mils. Reference 250.66 would give us a 3/0 cu.

Maybe the question is the physical size of the buss for 1000a. I do agree that it is a conductor.


George Little
#96526 12/13/05 10:46 AM
Joined: May 2004
Posts: 162
C
Member
The Chase Shawmut Book of Electrical Information indicates that a 4" X 1/4" Copper Bar can handel 1000A or 1000 A per Sq"

This information was in the NEC around 1971 or so and it indicated that Copper Bus could carry 1000A per Sq" and Aluminum could handel 700A per Sq"