1 members (Scott35), 565 guests, and 35 robots.
Page 4 of 5 1 2 3 4 5
Why can't the IG be terminated on the Nuetral bar of the service panel again?
250???
Dnk....
Okay- What are doing for transformer overcurrent?? I say we protect the primary at 125% of it's capacity and forgo protection of the secondary. If that's the case we can protect the primary at 125% x 90 = 112a. so we use a 125a overcurrent protection. gives me a #1/0 wire. Now we don't have to protect the secondary. This overcurrent protects the transformer. If we go over 125a. on the primary we would have to add secondary protection.
Added edit:
I'm going on the basis that we have a 480v. 3Ø primary and it is a 75kva xformer. Sorry bout that guys.
[This message has been edited by George Little (edited 09-09-2005).]
George Little
George, I prefer the same method you describe.
Ryan Jackson,
Salt Lake City
iwire Offline OP
Well that would depend on what the transformer is feeding.
If ut feeds a panel it is likely the panel will need protection and that might as well be incorporated into the transformer protection as well.
Ron Offline
Due to panelboard OCPD requirements, or just that there is a lot of 120V loads that due to load transfer/movement may result in a lot of imbalance for a short period of time, detection of a 120V overcurrent is made more accurate by secondary protection. Remember the primary to secondary is not bolted, so a significant single phase load change does not directly effect the primary current per phase in exactly the same ratios (ie primary phase A to secondary phase A).
Ron
Ron Offline
One other benefit of having the primary and secondary protection is the increased flexibility in the primary OCPD to grow larger (250% max) to overcome high inrush, possibly due to k-ratings or other design consideration.
Transformer inrush per ANSI standards is approximately 12xFLA or 1080A, so the primary breaker may trip, even if the actual load is low. Inrush is unrelated to actual connected load.
Edited for calculation error.
[This message has been edited by Ron (edited 09-09-2005).]
Ron
I would say the most "NEC-ish" problem in the Transformer Image would be the Grounding Electrode Conductor does not terminate directly to the "X-0" terminal.
Next would be the "what appear to be" too small EGCs - at least for the Secondary side's feeders the EGC looks a wee bit small.
Odd to me (at least) is the Phase arrangement here - more specific, the color code arrangement, vs. terminals.
Starting from the left, we have:
<OL TYPE=1>
[*] An "X" terminal tagged Blue (would be typically X-3),
[*] An "H" terminal tagged Orange (would be typically H-2),
[*] The common point of the Secondary coils - "X-0",
[*] An "X" terminal tagged Red (would be typically X-2),
[*] An "H" terminal tagged Brown (would be typically H-1),
[*] An "XH" terminal tagged Yellow (would be typically H-3),
[*] An "X" terminal tagged Black (would be typically X-1).
</OL>
Not that this is any violation, just kind of an odd arrangement to me.
Anyone find it strange?
Scott35
Scott, here is a self quote from my post on this."Question #2 is I cannot make out what is in the conduit on the bottom left side. It appears to be the gec. If so where is it terminated and would the bonding jumper sent to the bushing on that conduit entry need to be the same size as the gec? " I am still wondering if I am looking at this picture wrong, or am I missing something?
iwire Offline OP
Thanks everyone for the responses so far.
Scott noticed what I noticed, the GEC lands at the bonding point not on XO directly which IMO is a violation of the current wording in 250.30(A)(2)(a)
Just part of 250.30(A)(2)(a)
shall be used to connect the grounded conductor of the derived system to the grounding electrode
IMO as it is in the picture the GEC is being used to connect the bonding jumper to the electrode.
My HI buddy, I believe what we have is this.
1.25" primary feeder with EGC.
2" Secondary tap with EGC
The GEC conductor disappears into the back somewhere. It probably runs without conduit out one of the holes in the grill.
I had the advantage of seeing this much larger, I reduced the picture size before posting.
The way I do these is to install a triple lug on X0.
One conductor is the secondary grounded conductor (neutral).
The next conductor is the GEC.
The third is the bonding jumper.
I have "made do" with double lugs by passing the GEC through the terminal and bonding the tag end to the xfrmr case, but this comes very close to encroaching into the "No conductors above this point" area.
It looks to me like the GEC, which is landed in the group at the bottom left (There's only one conductor that I can't account for and it appears to be going through one of the slots in the transformer bottom) is undersize for GEC, possibly a #6.
Thanks for the thread, Bob. Some of my coworkers are still mystified by transformer grounding, and maybe this will help.