Recently red-tagged on a new-house construction because there was no GFCI protection for a receptacle on the wall opposite of a laundry-room sink. Inspector said all receptacles within 6' of the sink in any direction must have ground fault protection.
Not saying it isn't a good idea, but I couldn't find the article requiring it. 2002 NEC. Anyone have a reference?
-John
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#95274 09/06/05 06:48 PM
BigJohn, it is a new wording in 210.8(A)(7) of the 05 NEC.
Laundry, utility, and wet bar sinks — where the receptacles are installed within 1.8 m (6 ft) of the outside edge of the sink
If you are still under 02 the inspector is wrong.
Roger
#95275 09/06/05 06:49 PM
210.8 (a) (7) of 2005 NEC
#95276 09/06/05 06:52 PM
I snuck that one in on you John. [Linked Image]
Roger
#95277 09/06/05 06:56 PM
BigJohn Offline OP
I knew it. And I had to drive thirty miles to correct that bogus violation. [Linked Image]
Thanks, gentlemen.
-John
#95278 09/07/05 06:26 PM
Roger: