#94649 08/04/05 08:19 AM
Joined: Feb 2002
Posts: 2,233
H
Member
Does the pool filter motor have to be on a dedicated feed?
Can you install the convience receptacle on the same feed as the pool motor?
Any thoughts?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#94650 08/04/05 09:59 AM
Joined: May 2005
Posts: 706
T
Member
I don't find any requirement for the pool pump to be on a dedicated circuit without other outlets.

Dave

#94651 08/04/05 02:41 PM
Joined: Apr 2004
Posts: 60
M
Member
If the pool pump is hardwired, then this rule applies:

210.23(A)(2) Utilization Equipment Fastened in Place. The total rating of utilization equipment fastened in place, other than luminaires (lighting fixtures), shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied.

So if you want receptacles on a hard wired motor circuit, then it can only draw half of the circuit's rating (which isn't likely with most 120V pool pumps).


Mark
Kent, WA
#94652 08/04/05 03:15 PM
Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
The light circuit would be a better candidate for the receptacle but be aware of the "unspliced EGC" rule when you lay it out.
I pulled 2 EGCs when I did mine. The unspliced one went to the J box and another was used for the receptacle, switch etc.
My pump is 240v. I figure the I2R savings will pay for the extra few bucks I paid for the breaker ... eventually.


Greg Fretwell
#94653 08/04/05 03:37 PM
Joined: Jan 2002
Posts: 1,457
E
Member
680.22 (A) (3) "Dwelling unit(s). Where a permanently installed pool is installed at a dwelling unit(s), no fewer than one 125 volt 15 or 20 ampere receptacle on a general purpose branch circuit shall be located not less than 3.0m (10ft) from, and not more than 6.0 m (20ft) from, the inside wall of the pool."

I would say a circuit for the pool motor is not a general purpose branch circuit, thus the convienience receptacle can not be fed from that circuit.

#94654 08/04/05 04:58 PM
Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
Branch Circuit, General-Purpose. A branch circuit that supplies two or more receptacles or outlets for lighting and appliances.

I suppose it all depends on if a pool pump is an "appliance" and if the light is "lighting".
They didn't have any problem with my receptacle on the same circuit as the wet niche light. (Lee Co Fla)


Greg Fretwell
#94655 08/04/05 05:25 PM
Joined: Dec 2004
Posts: 1,064
D
Member
gfretwell, I don't understand the post about 2 equipment grounds and how that plays into line loss. I2R

Can you explain?


Dnk.....

#94656 08/04/05 05:58 PM
Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
With a 240v motor the loss in the wire will be less (increases with the square of current)
A wet niche light required an unspliced ground to the J box (with a few exceptions).
Since I was also feeding another circuit from this (the receptacles) it was easier to just pull 2 EGCs and avoid any confusion.


Greg Fretwell
#94657 08/04/05 06:11 PM
Joined: Dec 2004
Posts: 1,064
D
Member
Sorry, I didn't notice you switched topics in your post.

Somehow(I dunno),I thought you were suggesting an EGC had something to do with line loss.


Dnk......

#94658 08/04/05 10:48 PM
Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
I will plead temporary insanity. I was digging in the yard and I was delerious when I came back in to post that. ;-)

Sorry for the confusion.


Greg Fretwell