there must be six feet from outlet on outside of house to the tub correct?
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#94096 07/06/05 04:43 PM
Five feet
#94097 07/06/05 07:30 PM
10 feet.
And it's mandatory to have one between 10'- 20'.
Outdoor spas are treated the same as pools.
Speedy Petey
"Anyone who has never made a mistake has never tried anything new." -Albert Einstein
#94098 07/06/05 08:51 PM
Oops I'm a dummy. Was thinking indoor installation.
#94099 07/07/05 02:13 AM
thanks guys...
this site is cool!!!
#94100 07/07/05 02:28 AM
speedy can you quote nec art # for the 10-20'
rule thanks
h2o
#94101 07/07/05 12:56 PM
680.22(A)(3) Dwelling Unit(s). Where a permanently installed pool is installed at a dwelling unit(s), no fewer than one 125-volt 15- or 20-ampere receptacle on a general-purpose branch circuit shall be located not less than 3.0 m (10 ft) from and not more than 6.0 m (20 ft) from the inside wall of the pool. This receptacle shall be located not more than 2.0 m (6 ft 6 in.) above the floor, platform, or grade level serving the pool.