#93827 06/18/05 05:24 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Does the insulated #8 grounding conductor inside the PVC conduit connected to the back of a wet niche fixture need to be green in color?


George Little
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#93828 06/18/05 10:52 PM
Joined: Feb 2005
Posts: 693
L
Member
No, according to 680.23(B)(2)(a), but 250.119 seems to say yes.


Larry Fine
Fine Electric Co.
fineelectricco.com
#93829 06/19/05 06:15 AM
Joined: Jun 2004
Posts: 613
S
Member
The 2005 NEC recognizes this conductor for its fuction..."a bonding jumper" and therefore would not be required to be green in color...

shortcircuit

#93830 06/19/05 08:48 AM
Joined: Jan 2004
Posts: 1,507
G
Member
I wish the Code panel would make up their mind on what that #8 wire is called. The '02 calls it a grounding conductor and so the color code would kick in but, the '05 calls it a bonding conductor and the color code would not apply???IMHO.


George Little
#93831 06/19/05 01:09 PM
Joined: Jan 2005
Posts: 5,445
Likes: 3
Cat Servant
Member
The NEC is full of confusion...the old 'grounding or bonding' issue abounds.
As a "simple mans' rule,' when I get confused I ask myself "is this wire for lightning protection?" If so, then it's a 'ground.' If not, it's a 'bond."

Using this understanding, let's consider the wire from the panel to the water pipe.
In an old house, where there is no ground rod, this is a 'ground wire' or GEC.
In a new house, this wire is there to clear any fault current to the plumbing- so it's a bond, not a ground.

Probably over-simple, but it does help me keep focused.

#93832 06/26/05 11:20 PM
Joined: Feb 2005
Posts: 693
L
Member
I'd say that, since the conductor does not require being brought back to the panel feeding the equipment (if any), and is for minimizing gradients, it's a bonding conductor.


Larry Fine
Fine Electric Co.
fineelectricco.com
#93833 06/28/05 12:15 AM
Joined: Jun 2005
Posts: 91
G
Member
Quote
I wish the Code panel would make up their mind on what that #8 wire is called.
How about "Pool Gradient Conductor." Sounds official, and really can't be confused with an EGC. [Linked Image]


-George
#93834 06/28/05 01:35 AM
Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
Shortcircuit has it. There was an error in the code when they called the #8 in the pipe to the forming shell a grounding conductor and it was fixed in the 2005 code.
There were 4 proposals that all said essentially the same thing (17-93, 4, 5