Does the insulated #8 grounding conductor inside the PVC conduit connected to the back of a wet niche fixture need to be green in color?
George Little
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
No, according to 680.23(B)(2)(a), but 250.119 seems to say yes.
Larry Fine Fine Electric Co. fineelectricco.com
|
|
|
|
Joined: Jun 2004
Posts: 613
Member
|
The 2005 NEC recognizes this conductor for its fuction..."a bonding jumper" and therefore would not be required to be green in color...
shortcircuit
|
|
|
|
Joined: Jan 2004
Posts: 1,507
OP
Member
|
I wish the Code panel would make up their mind on what that #8 wire is called. The '02 calls it a grounding conductor and so the color code would kick in but, the '05 calls it a bonding conductor and the color code would not apply???IMHO.
George Little
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 2
Cat Servant Member
|
The NEC is full of confusion...the old 'grounding or bonding' issue abounds. As a "simple mans' rule,' when I get confused I ask myself "is this wire for lightning protection?" If so, then it's a 'ground.' If not, it's a 'bond."
Using this understanding, let's consider the wire from the panel to the water pipe. In an old house, where there is no ground rod, this is a 'ground wire' or GEC. In a new house, this wire is there to clear any fault current to the plumbing- so it's a bond, not a ground.
Probably over-simple, but it does help me keep focused.
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
I'd say that, since the conductor does not require being brought back to the panel feeding the equipment (if any), and is for minimizing gradients, it's a bonding conductor.
Larry Fine Fine Electric Co. fineelectricco.com
|
|
|
|
Joined: Jun 2005
Posts: 91
Member
|
I wish the Code panel would make up their mind on what that #8 wire is called. How about "Pool Gradient Conductor." Sounds official, and really can't be confused with an EGC.
-George
|
|
|
|
Joined: Jul 2004
Posts: 9,923 Likes: 32
Member
|
Shortcircuit has it. There was an error in the code when they called the #8 in the pipe to the forming shell a grounding conductor and it was fixed in the 2005 code. There were 4 proposals that all said essentially the same thing (17-93, 4, 5 & 6)