Safety at heights?
1 members (Scott35), 425 guests, and 10 robots.
CRW Offline OP
The 2002 (accidently) prohibits the practice. The 2005 permits it.
What does the 2002 prohibit, and where is that specifically?
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
Raceway article(s) xxx.22 say that you can put a cable in a raceway if the cable article allows it. The only cable articles that allow this are 330 for MC (330.10) and 328 for medium voltage.
Ryan Jackson,
Salt Lake City
CRW Offline OP
Thanx Ryan, I had never seen that before. Actually, the application I was involved in, with Type TC WAS permitted in 2002 (336). But the issue started an argument involving all cable types in general, and your point addresses that. So my question now is, was there any prohibition PREVIOUSLY to putting various cables in conduits or raceways if they weren't specifically permitted?