Does a duplex receptacle still count for general lighting receptacles per 210.52(A)(within 6 feet of any spot on the wall) if the receptacle is switched (both halves)as allowed by 210.70(A)(1)exc.1? Or, is it required to split the duplex receptacle into one outlet always hot and the other switched?
Earl
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
Looks legal to me, although perhaps a bad design
Greg Fretwell
|
|
|
|
Joined: Jun 2003
Posts: 1,143
Member
|
I don't recall the Code excluding switched receptacles... it just says that they have to be the minimum distance (12') apart, or 6' from any point along a wall.
Nothing about always hot.
|
|
|
|
Joined: Jun 2004
Posts: 613
Member
|
If you switch the top and bottom of a duplex receptacle, it becomes a lighting outlet and would not meet the requirements on spacing for receptacle outlets as specified in 210.52(A)(1)
So...common practice is to switch half of the receptacle outlet in a room to meet the requirements of both 210.52(A)(1) and 210.70(A)(1)
It is not required to be split,but if you don't you must also locate a "Live" receptacle outlet next to the switched lighting outlet to meet the spacing requirements.
My practice is to switch the top half so when the homeowner plugs in a cordless phone with those little square power transformers it does not cover the other half of the receptacle.
shortcircuit
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
shortcircuit, If you switch the top and bottom of a duplex receptacle, it becomes a lighting outlet and would not meet the requirements on spacing for receptacle outlets as specified in 210.52(A)(1) Please cite the code section that says this. Thanks.
Don(resqcapt19)
|
|
|
|
Joined: May 2004
Posts: 162
Member
|
Short Circuit
That is a Mass Amendment!
Charlie
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
Don- I believe that's called a "vest pocket" rule" Also, I think DougW meant to say "maximum" in stead of "Minimum 12 feet." in his comment.
George Little
|
|
|
|
Joined: May 2004
Posts: 162
Member
|
George Please explain "vest pocket"??
Charlie
|
|
|
|
Joined: Dec 2004
Posts: 329
Member
|
quote: -------------------------------------------------------------------------------- If you switch the top and bottom of a duplex receptacle, it becomes a lighting outlet and would not meet the requirements on spacing for receptacle outlets as specified in 210.52(A)(1) -------------------------------------------------------------------------------- I don't think that is an NEC requirement. Down here in Central FLA none of the outlets I have seen are split switched, the room light switch operates the whole duplex. Ian
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
Ian, I suppose it is just regional, even when we are on exactly the same code. In Lee County Fl. they want "half hots" but I doubt they actually check close enough to catch folks 99.999% of the time. Inspectors are so overworked around here I wonder how they find anything. (30 or more a day) A agree there is no clear code language to enforce it.
Greg Fretwell
|
|
|
Posts: 99
Joined: August 2003
|
|
|
|
|