If a hot tub is installed on a screened porch of a dwelling and fed with a 50 amp GFCI protected circuit, is a disconnect required near the hot tub?
The 50 amp GFCI breaker isn't within sight of the tub.
shortcircuit
|
|
|
|
Joined: Jan 2002
Posts: 1,457
Member
|
Yes disco is needed. 680.12
|
|
|
|
Joined: Jun 2004
Posts: 613
OP
Member
|
Thanx Electricmanscott...wish they would put that requirement in part 4 also to clear up the confusion that I get from the emergency shutoff rule(680.41)
shortcircuit
|
|
|
|
Joined: Aug 2001
Posts: 466 Likes: 1
Member
|
The emergency disconnect is not required at single family dwellings.
|
|
|
|
Joined: Mar 2004
Posts: 814
Member
|
Jim, you're correct that the emergency disco is not required for single family dwellings however the SERVICE disconnect is still required to be within sight just like any other piece of equipment.
|
|
|
|
Joined: Feb 2002
Posts: 2,233
Member
|
What if there is circuit breakers or switches under the skirt that will disconnect the motor. Do they count?
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
Yes, the disconnect(s) under the skirt of the spa or hot tub qualify as the required disconnect(s). They/it certainly would be within sight of the equipment served. Some have said that an additional disconnect is needed within sight of the spa or hot tub. The '02 code seems to make it a lot clearer to me by saying "within sight of it's equipment" 680.12 and not "within sight from all pools, spas, and hot tub equipment and shall be located 5' from the inside of the pool, spa, or hot tub" as it did in the '99
George Little
|
|
|
|
Joined: Jun 2004
Posts: 613
OP
Member
|
George, I think that the disconnect required by 680.12 should be seperate from the tub altogether.What if the hot tub is defective and they want to remove it and replace it with a new one?
shortcircuit
|
|
|
|
Joined: Jan 2005
Posts: 9
Junior Member
|
680.12 says the disconnecting means shall be accessible & within sight from its equipment
look at the definition of accessible, I do not think the disconnect under the spa meets that requirement.
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
Wait a minute here- Are we trying to say that the disconnect under the skirt of a spa is not "accessible and within sight of it's equipment" 680.12? I would think that if I'm working on the equipment associated with the disconnect, that I would have the spa/hot tub opened up and this would provides accessibility and within sight. The relationship is between the disconnect and the equipment. You want to install an additional disconnect within sight of the spa/hot tub? Go for it. I'd like to bid against you.