#91238 01/06/05 07:21 AM
Joined: Jun 2004
Posts: 613
S
Member
If a hot tub is installed on a screened porch of a dwelling and fed with a 50 amp GFCI protected circuit, is a disconnect required near the hot tub?

The 50 amp GFCI breaker isn't within sight of the tub.

shortcircuit

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#91239 01/06/05 08:29 AM
Joined: Jan 2002
Posts: 1,457
E
Member
Yes disco is needed. 680.12

#91240 01/06/05 09:41 AM
Joined: Jun 2004
Posts: 613
S
Member
Thanx Electricmanscott...wish they would put that requirement in part 4 also to clear up the confusion that I get from the emergency shutoff rule(680.41)

shortcircuit

#91241 01/06/05 11:19 PM
Joined: Aug 2001
Posts: 466
Likes: 1
J
Member
The emergency disconnect is not required at single family dwellings.

#91242 01/06/05 11:38 PM
Joined: Mar 2004
Posts: 814
B
Member
Jim, you're correct that the emergency disco is not required for single family dwellings however the SERVICE disconnect is still required to be within sight just like any other piece of equipment.

#91243 01/10/05 10:46 PM
Joined: Feb 2002
Posts: 2,233
H
Member
What if there is circuit breakers or switches under the skirt that will disconnect the motor. Do they count?

#91244 01/11/05 12:16 AM
Joined: Jan 2004
Posts: 1,507
G
Member
Yes, the disconnect(s) under the skirt of the spa or hot tub qualify as the required disconnect(s). They/it certainly would be within sight of the equipment served. Some have said that an additional disconnect is needed within sight of the spa or hot tub. The '02 code seems to make it a lot clearer to me by saying "within sight of it's equipment" 680.12 and not "within sight from all pools, spas, and hot tub equipment and shall be located 5' from the inside of the pool, spa, or hot tub" as it did in the '99


George Little
#91245 01/11/05 06:52 AM
Joined: Jun 2004
Posts: 613
S
Member
George, I think that the disconnect required by 680.12 should be seperate from the tub altogether.What if the hot tub is defective and they want to remove it and replace it with a new one?

shortcircuit

#91246 01/11/05 08:09 PM
Joined: Jan 2005
Posts: 9
M
Junior Member
680.12 says the disconnecting means shall be
accessible & within sight from its equipment

look at the definition of accessible, I do
not think the disconnect under the spa meets
that requirement.

#91247 01/12/05 12:19 AM
Joined: Jan 2004
Posts: 1,507
G
Member
Wait a minute here- Are we trying to say that the disconnect under the skirt of a spa is not "accessible and within sight of it's equipment" 680.12? I would think that if I'm working on the equipment associated with the disconnect, that I would have the spa/hot tub opened up and this would provides accessibility and within sight. The relationship is between the disconnect and the equipment. You want to install an additional disconnect within sight of the spa/hot tub? Go for it. I'd like to bid against you.


George Little