Hi, Is there ever a time where a MAIN PANELBOARD for a Sinfgle Fam Dwelling would NOT have a #4 bare ground for cold water ground? copper piping.
here in Arkansas the GEC goes from the Ground rod to the METER BASE. In Kentucky it is from the Panelboard to the Ground Rod. If there is a copper water line, you need a COLD WATER BOND..usually a #6 for 100A and #4 for 200A this ALWAYS goes to the MAIN PANELBOARD..
i saw a house today that only had a gec from the main disc at the meter..no other ground in the panel..
this looked wrong to me..
the feed was a 4 conductor SER type cable..
thanks for any replies..
mustang
|
|
|
|
Joined: May 2004
Posts: 697
Member
|
Allways check with the AHJ.
Dave
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
GEC's are required to go from the electrode to the service equipment. If the disco at the meter is the service equipment, and it sounds like it is, this is code compliant.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
It can be anywhere from the load end of the drop to the disconnect enclosure.
250.24 Grounding Service-Supplied Alternating-Current Systems. (A)(1) General. The connection shall be made at any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means.
Greg Fretwell
|
|
|
|
Joined: Feb 2002
Posts: 2,233
Member
|
What if all of the water piping in the house is PLASTIC? What do you ground to?
|
|
|
Posts: 75
Joined: June 2012
|
|
|
|
|