#8919 04/09/02 11:17 PM
HI Dan,
Thanks for being here!
240.6 on Standard Ampere Ratings for fuses and fixed-trip cb's is pretty well self-explanatory. But, why a fuse with a standard ampere rating of 601 Amps? Is this a special application of some type?
Thanks in advance!
#8920 04/10/02 09:37 AM
Great Q!
I always thought that was a typo... and how could they possibly tell the difference between a 600 and a 601? (Put >601A on it and the 601 will open first?)
-Virgil
5 Star Inspections
Member IAEI
#8921 04/12/02 12:34 PM
Randy,
That is probably one of the most asked questions when it comes to fuses. In fact I had the same question last week.
The reason there is a 601 fuse is to give flexibility. Class R and J fuses only go up to 600A. Above 600A, a Class L fuse must be used. Class L fuses range from 601A-6000A. The first case size of a listed Class L fuse is 800A with fuses sizes typically of 601, 650, 700, 750 and 800A.
Thus, if you have a circuit that could be sized at 600A, but may have to be increased in the future due to future expansion or motor inrush issues, Class L is the obvious choice. By going with a 601A Class L fuse, in an 800A disconnect, the fuses could be increased in the future up to 800A, provided conductors with an appropriate ampacity are used.
Thanks,
Dan
#8922 04/12/02 11:22 PM
Dan,
Thanks, as usual, when one finally understands the "why's", it's easier to remember...
Now it makes sense...
-Virgil
5 Star Inspections
Member IAEI