0 members (), 433 guests, and 18 robots.
#88388 05/30/04 08:28 PM
If I am installing conductors larger than #6 in conduit that enters one side of a wireway and exits the opposite side and the conductors are only deflected 25°, is this considered to be a straight pull and the rules at 314.28 apply? If they do and if I'm using 2" conduit, the wireway would have to be 16" between the two sides.
George Little
#88389 05/30/04 09:11 PM
Hi George,
Depends.....
What do you mean by a "wireway"?
Dave
#88390 05/30/04 09:17 PM
Wireway as defined in NFPA 70, 2002edition, Article 376. Sorry for the formal reference but I don't know any other way to put it :-)
George Little
#88391 05/30/04 09:33 PM
376.23 Insulated Conductors.(B) Handbook Commentary: Section 376.23(B) was added to the 2002 Code to ensure adequate space for conductors in other raceways as they enter a wireway. Where wireways are used as pull boxes, the same minimum dimension requirements associated with raceway entries of pull boxes apply.
Kind of looks like your stuck with 314.28!
Dave