R
Member
OK ,I have a 200amp service residential.I have a out building/workshop with a 100 amp main breaker panel installed. Now can I run 3 wire service to it?Bond neutral to can.
Do I place a rod there or not?
Do I run 4 wire and place rod?
I re read some past threads but need alittle
reassurance.Thanks in advance.
using direct burial cable pvc conduit.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Aug 2003
Posts: 1,374
R
Moderator
Are there any continuos metal paths between the building? Such as water pipe, gas, coax, phone, etc...?


Ryan Jackson,
Salt Lake City
Joined: Apr 2002
Posts: 178
R
Member
Not that I`m aware of at this time.I read 250.32 Not clear on the single branch part.Electricians here say you can run three wire but the best way would be go with 4 wire and the rod.Just would like to better understand if three wire is permisable in this situation legally. But also personally I`m lean towards the best way if it is better.

Joined: Apr 2003
Posts: 139
B
Member
If your installing a panelboard at the workshop, than you don't have a single branch circuit going to the workshop, you have a feeder.

Regardless if you wire with 3-wire or 4-wire, a grounding electrode system will be required at the workshop building.

I don't think either way can be classified as "better". Both will provide adequate service and practical safegaurding.


Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter
Joined: Apr 2002
Posts: 197
T
Member
Take a course on stray voltage and you will find out why the 4-wire method IS better than using only 3.

If you are not sure of metallic paths then you MUST use 4-wire.

Ground rod(s) are necessary at the second building.