#88266 05/25/04 06:07 PM
This is a 200a 1ph. UG residential service.
No metallic water lines,interior or exterior. Meterbase is back to back with a 200a main brkr. panel. Short pvc nipple between them. # 4 solid copper from lug in MB down to 2 ground rods 6' apart.
No Ahj here. Homeowner hired a retired elec inspector to look at job and he says the #4 must come from the panel.
Can anyone give me a code art.for this?
Russell
#88267 05/25/04 06:15 PM
Hello Russell, It sounds as though this retired inspector is from an area that is not used to seeing this connection at the meter.
Roger
[This message has been edited by Roger (edited 05-25-2004).]
#88268 05/25/04 06:29 PM
Hi Roger.
Thats what I thought. I don't see the difference in this situation.
Russell
#88269 05/25/04 09:18 PM
Russell,
The connection to a ground rod doesn't need anything larger than #6 Copper. Nothing wrong with the #4 of course. [Linked Image]
Peter
Peter
#88270 05/25/04 09:47 PM
You're right CT. It's just a habit. [Linked Image]
[This message has been edited by ga.sparky56 (edited 05-25-2004).]
#88271 05/27/04 11:13 PM
Here in Washington, the meter base is not considered to be accessible to the occupant. Technically, the power company says you need to call and coordinate cutting the seal, there its not really accessible. Therefore, the GEC can not be run from there.
This is a AHJ call, and not an NEC code rule except for a strict interpretation of 250.68 which says the GEC must be accessible.