#87585 03/21/04 01:12 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
For a seperatley derived system, 250.30(A)(4) tells us to use the closest available electrode that is either water pipe or building steel. I agree with you, 99% of the time the steel will be signifigantly closer than the portion of the water pipe that meets the definition of an electrode.


Ryan Jackson,
Salt Lake City
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#87586 03/21/04 01:24 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Again we have a mix of code articles, actually almost the same ones.

250.30 Grounding Separately Derived Alternating-Current Systems.
Quote
250.30(A)(4) Grounding Electrode. The grounding electrode shall be as near as practicable to and preferably in the same area as the grounding electrode conductor connection to the system. The grounding electrode shall be the nearest one of the following:
(1) An effectively grounded structural metal member of the structure
(2) An effectively grounded metal water pipe within 1.5 m (5 ft) from the point of entrance into the building

250.104 Bonding of Piping Systems and Exposed Structural Steel.
Quote
250.104(A)(4) Separately Derived Systems. The grounded conductor of each separately derived system shall be bonded to the nearest available point of the interior metal water piping system(s) in the area served by each separately derived system. This connection shall be made at the same point on the separately derived system where the grounding electrode conductor is connected. Each bonding jumper shall be sized in accordance with Table 250.66.

Exception: A separate water piping bonding jumper shall not be required where the effectively grounded metal frame of a building or structure is used as the grounding electrode for a separately derived system and is bonded to the metallic water piping in the area served by the separately derived system.

I will be honest I have never seen anyone around here comply with 250.104(A)(4) [Linked Image]

Bob

[This message has been edited by iwire (edited 03-21-2004).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#87587 03/21/04 01:56 PM
Joined: Mar 2004
Posts: 5
P
Junior Member
I think we're getting to it!. How can 250.50 and 250.30 match. If we can't use the CW pipe as an grounding electrode, then how do we meet the specifics of each section?

#87588 03/21/04 02:05 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
Parcours: I think it all boils down to availability. If the water pipe is not available as an electrode, you still have to bond it so that it can't become energized. If it is available, you must use it in an effort to create a better grounding electrode system.

If the water pipe isn't available for your SDS, use a different electorde! [Linked Image]


Ryan Jackson,
Salt Lake City
#87589 03/22/04 08:44 AM
Joined: Jun 2003
Posts: 681
P
Member
Scott
That warm California air must be getting to you [Linked Image]

Pierre


Pierre Belarge