Posted By: parcours Cold Water Pipe Bond - 03/20/04 11:05 PM
I understand why all interior metallic piping must be bonded, but why is the water pipe required to be bonded within the first 5' of the point of entrance to a facility?
Posted By: Ryan_J Re: Cold Water Pipe Bond - 03/20/04 11:19 PM
The reason is that teh NEC does not trust plumbers.

We don't a copper section of pipe that we are depending upon for our ground to be replaced with a non metallic type. The liklihood of this occuring is lessened by requiring the bond to be closer to the entrance of the building.
Posted By: electure Re: Cold Water Pipe Bond - 03/21/04 03:00 AM
I gave "super" jumper cables to a couple of my plumber friends for Christmas.
(Cheap guy that I am, 1 set was good for 2 plumbers).
They often cut waterlines in older homes (with bonds that were installed before the 5' rule, [we used to bond them to the CW in the water heater closet] and old services were only bonded to cold water) in order to install T fittings or make repairs.
When they're under a house (older homes are of a raised wood floor design, with no basement) drenched in water, I just feel better knowing that they won't become a statistic if the house has a bad neutral.
The 5' rule increases their safety too...S



[This message has been edited by electure (edited 03-20-2004).]
Posted By: Edward Re: Cold Water Pipe Bond - 03/21/04 05:16 AM
Here is my understanding: Guys correct me if I am wrong.
When the bond is within 5 feet (visible not under the house) This way the chance of the first 5 feet of the pipe being replaced by a plastic is very low AND If That Does Happen then the metal city supply will be long enough for it to have a low resistance or supplement the ground rod.

Am I correct?

Edward
Posted By: Ryan_J Re: Cold Water Pipe Bond - 03/21/04 05:59 AM
Hi Edward. I think that for the most part you are correct, but I think that if the copper is replaced with plastic between the earth and your wire's connection to the pipe, there is nothing that would give it the path to earth that is required. [Linked Image]
Posted By: Edward Re: Cold Water Pipe Bond - 03/21/04 06:05 AM
Ryan,
Having your statement in mind, then does it still matter where you bond if your main water line is PVC? It does not matter does it?

Edward
Posted By: Scott35 Re: Cold Water Pipe Bond - 03/21/04 07:34 AM
Edward;

Quote

then does it still matter where you bond if your main water line is PVC?

In this case, you Bond the incoming Cold Water Supply Piping to the GES, with a Poly Ethylene Pull rope - sized per 250-66.
Yellow Pull Rope is preferred, but not mandatory...

[Add Cheezy Drumroll, ended by Cymbal Splash]

Sorry, I could not resist that one! [Linked Image]

Scott35
Posted By: parcours Re: Cold Water Pipe Bond - 03/21/04 03:55 PM
OK.. But he NEC allows that CW bond to be beyond the 5' if they customer is not going to install a transformer and tie GEC to the CW. Case in point, just like an earlier post that bonded the CW within the hot water heater closet. You can still do that in a non-commercial, non-industrial application.
I understand the concept of re-piping, I guess that having the first 5' covered is the intent of the code?
Posted By: iwire Re: Cold Water Pipe Bond - 03/21/04 04:28 PM
I think we are mixing two separate but related code requirements.

First is 250.52(A)(1)

Quote
250.52 Grounding Electrodes.
(A) Electrodes Permitted for Grounding.
(1) Metal Underground Water Pipe. A metal underground water pipe in direct contact with the earth for 3.0 m (10 ft) or more (including any metal well casing effectively bonded to the pipe) and electrically continuous (or made electrically continuous by bonding around insulating joints or insulating pipe) to the points of connection of the grounding electrode conductor and the bonding conductors. Interior metal water piping located more than 1.52 m (5 ft) from the point of entrance to the building shall not be used as a part of the grounding electrode system or as a conductor to interconnect electrodes that are part of the grounding electrode system.

This is not bonding, this is grounding the service to the water main and this must be done within 5' of entrance of the water pipe.

But what if you have a plastic water main and metallic piping inside after the meter.

Now bonding is what we are doing and we follow 250.104(A)

Quote
250.104 Bonding of Piping Systems and Exposed Structural Steel.
(A) Metal Water Piping. The metal water piping system shall be bonded as required in (1), (2), (3), or (4) of this section. The bonding jumper(s) shall be installed in accordance with 250.64(A), (B), and (E). The points of attachment of the bonding jumper(s) shall be accessible.

It happens that if we ground the service to a metal water main and jump the meter we have also bonded metal water pipes in the building, if jumpers are installed across insulating sections, like the plastic housing of a water filter or maybe the water heater.

So;

Grounding a service to a metal water service must be done in the first five feet.

Bonding metal water pipes can be done anywhere.

Many times both code articles are complied with at the same time.

Clear as Mud?

Bob
Posted By: parcours Re: Cold Water Pipe Bond - 03/21/04 05:03 PM
Bob, this has been my take on this subject. In addition, you are correct, bonding and grounding are always confused.
Here's another one, based on 250.104, why do electrical inspectors insist on grounding the neutral on a separately derived system to the CW, rather then building, even if building steel is available? Clearly this is a violation.
Posted By: Ryan_J Re: Cold Water Pipe Bond - 03/21/04 05:12 PM
For a seperatley derived system, 250.30(A)(4) tells us to use the closest available electrode that is either water pipe or building steel. I agree with you, 99% of the time the steel will be signifigantly closer than the portion of the water pipe that meets the definition of an electrode.
Posted By: iwire Re: Cold Water Pipe Bond - 03/21/04 05:24 PM
Again we have a mix of code articles, actually almost the same ones.

250.30 Grounding Separately Derived Alternating-Current Systems.
Quote
250.30(A)(4) Grounding Electrode. The grounding electrode shall be as near as practicable to and preferably in the same area as the grounding electrode conductor connection to the system. The grounding electrode shall be the nearest one of the following:
(1) An effectively grounded structural metal member of the structure
(2) An effectively grounded metal water pipe within 1.5 m (5 ft) from the point of entrance into the building

250.104 Bonding of Piping Systems and Exposed Structural Steel.
Quote
250.104(A)(4) Separately Derived Systems. The grounded conductor of each separately derived system shall be bonded to the nearest available point of the interior metal water piping system(s) in the area served by each separately derived system. This connection shall be made at the same point on the separately derived system where the grounding electrode conductor is connected. Each bonding jumper shall be sized in accordance with Table 250.66.

Exception: A separate water piping bonding jumper shall not be required where the effectively grounded metal frame of a building or structure is used as the grounding electrode for a separately derived system and is bonded to the metallic water piping in the area served by the separately derived system.

I will be honest I have never seen anyone around here comply with 250.104(A)(4) [Linked Image]

Bob

[This message has been edited by iwire (edited 03-21-2004).]
Posted By: parcours Re: Cold Water Pipe Bond - 03/21/04 05:56 PM
I think we're getting to it!. How can 250.50 and 250.30 match. If we can't use the CW pipe as an grounding electrode, then how do we meet the specifics of each section?
Posted By: Ryan_J Re: Cold Water Pipe Bond - 03/21/04 06:05 PM
Parcours: I think it all boils down to availability. If the water pipe is not available as an electrode, you still have to bond it so that it can't become energized. If it is available, you must use it in an effort to create a better grounding electrode system.

If the water pipe isn't available for your SDS, use a different electorde! [Linked Image]
Posted By: PCBelarge Re: Cold Water Pipe Bond - 03/22/04 12:44 PM
Scott
That warm California air must be getting to you [Linked Image]

Pierre