O.K., usual disclaimers: Johnny Foreigner, not on intimate terms with the intricacies of the language used in the NEC, etc.
I haven't had a chance to scan the NEC for other articles that might affect this argument, but based on those cited in this thread I have to agree with Don's interpretation that there is nothing to say that the GEC cannot be green.
As a first step I double checked on the NEC definitions of GEC and EGC just in case I was missing something. In fact I was wondering if the term equipment grounding conductor could be taken to include the GEC, thereby making use of green (or green/yellow or bare) mandatory for the GEC, but no, the NEC definition of the EGC makes it clear that it does not include the GEC.
200.7 reserves the colors white and gray for use as grounded circuit conductors only. It seems everybody is agreed that the GEC cannot, therefore, be white or gray.
250.119 specifies the methods that must be used to identify an EGC. It makes no mention of the GEC, neither does it specify that green (or green/yellow) must not be used for conductors other than an EGC.
310.12(B) seems to be a superfluous entry to me. It just says that equipment grounding conductors must comply with 250.119. Again, no mention whatsoever of the GEC, either directly or by cross-reference to 250.119.
It does seem that 310.12(C) might indeed prevent plain black from being used as the GEC if black is used as an ungrounded (phase) conductor in the installation (as it almost certainly will be). This rule just catches what colors may NOT be used for the GEC if that same color is already in use as an ungrounded conductor. It in no way says that green may not be used for a GEC (unless green is being used as a phase somewhere!).
310.12(C) just mentions "distinguishable" rather than colors. Presumably this would allow black to be used as the GEC if it were suitably tagged at regular intervals, thereby making it easily distinguishable from a plain black ungrounded conductor. Marking with green tape seems to be the easiest way to achieve this.
Sorry Joe, but I don't see how 250.119 and 310.12(B) that you cited could be interpreted in any way as to make it a violation to use green for the GEC. Could you explain how you come to this interpretation?
From near the top of this thread:
His 310-12 proposal was to identify the GEC with "green marking" and Code Panel 5 rejected it, and their reason was that the GEC can be any color you want except white, gray, or green.
They also said that if the installer didn't know what it was, that they had no business being in the enclosure.
OK, I'm not familiar with the way these Code Panels operate, but what did they cite to backup their assertion that the GEC may not be green? 200.7 clearly specifies, by exclusion, that the GEC cannot be white or gray, but there's still nothing there to say it cannot be green.
I agree with the last part of the quote. The GEC and other bonding cables should be obvious as to their function whatever color they may be. Even if some interpretation of the NEC meant that green was not permitted for the GEC, would anybody argue that such use could constitute a safety problem?
To paraphrase that last quote, if the installer doesn't understand the purpose of a green-colored GEC at the busbar, he still has no business being inside the panel.
An afterthought: There doesn't seem to be anything which specifies that green cannot be used as an ungrounded conductor, except for 310.12(C) which would prhibit such use if green is used for the EGC. Does this mean that if all EGCs are left bare or identified green/yellow that plain green could be used as a hot?
[This message has been edited by pauluk (edited 03-09-2003).]