ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 516 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#82939 12/22/02 08:51 PM
Joined: Apr 2002
Posts: 13
G
gisbon Offline OP
Member
Could someone please tell me the NEC article which states the line has to be on top and load on the bottom of a breaker or disconnecting means. I have done it that way forever and now need to prove where it is located in the NEC. Or is it?

Thank You,
Tom

Merry Christmas to all and a very safe Holiday.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#82940 12/22/02 10:33 PM
Joined: Apr 2002
Posts: 197
G
Gwz Offline
Member
That is not in the NEC, BUT

If the CB is marked " Line " then the incoming power is connected to the " Line " terminals of the CB what-ever the position ( top, bottom, sideways. 110.3(B).

#82941 12/22/02 10:34 PM
Joined: Nov 2002
Posts: 267
W
Member
My understanding of line load was always manufacturers specs. I might be wrong but I don't belive there is anything in the code book for this.

#82942 12/22/02 11:49 PM
Joined: Apr 2002
Posts: 7,382
Likes: 7
Member
IMHO, think about this:
The "line" side of a fused disconnect is connected to the bottom lugs.....you "open" the disco to replace a fuse....the fuse is "hot", and so are the knives that you opened.....

How many of us have come upon this scenario??

Just put a untrained person, DIY'er, homwowner, or the new apprentice in the above situation!

How about the guys that "back feed" a 2 or 3 pole CB???

Manufacturers instructions are supposed to be followed. Somewhere there is/was a reference about the disconnect switch isolating the fuses when the switch was "open".

John


John
#82943 12/23/02 10:19 AM
Joined: Nov 2002
Posts: 267
W
Member
One old reference in the code to all knife blade disconnects not to be installed as to allow gravity to close them.

#82944 12/26/02 09:54 PM
Joined: Mar 2001
Posts: 2,056
R
Member
Article 404.7 requires that on vertically mounted swiches the up position of the handle shall be the on position.
I also recall the explanation that refers to gravity tending to open a switch as opposed to closing it.

#82945 12/27/02 08:49 AM
Joined: Dec 2000
Posts: 4,294
Member
HotLine's post brings up another point.
When testing (always) disconnects and breakers, be sure to not only test line to ground, but line to line as well, lest you run into an ungrounded delta system that will show no voltage to ground (but might be hot 480).
Some of the younger folks have worked just on Y systems, and the delta never even seems to enter their minds.
Just the thought of it makes me ill [Linked Image]...S


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5