I heard someone refer to the line and load terminals of a CB as primary side and secondary side? Is this common terminology?
Redsy Don't know if it is common or not, but I have used that terminology when discussing lines and loads with Lead Engineers and some contractors.
Redsy:
The UL Directory "White Book" includes the following statement under the heading of "LINE - LOAD CONNECTIONS"
"Line and load markings on a circuit breaker are intended to limit connections thereto as marked."
Watch out four for backfed installations, if you need more information from the "White Book" let me know.
[This message has been edited by Joe Tedesco (edited 03-13-2002).]
Posts: 440 Likes: 3
Never heard of it relative to breakers. Always hear it relative to transformers.
Regards, Doc
The Watt Doctor Altura Cogen Channelview, TX