Several circuits of 12470, running thru manholes, deadbreak elbows in junctions, metal ladder , metal cable supports, Ground bar, two ground rods, all grounds and shields tied together.Sound Ok???
Omission of an {often} bare-copper conductor in the same raceway with the phase cables may accelerate damage {in fault situations} to the tape/drain-wire shield under the MV-cable jacket. The additional grounding conductor is routine, well-considered boilerplate for many.
[This message has been edited by Bjarney (edited 10-17-2002).]
Guys Theres two 500mcm in the concrete of the duct bank to each manhole and tied to the groundinging bar in each manhole. As far as designing eng. We;re it.
Someone may be sniveling about expecting to see “IEEE std 837”-grade connections, but that's not an NEC or NESC requirement. [If it's specified in contract documents, that's a whole 'nother matter.] http://www.fciconnect.com/products/technical_01_01_02.asp