Posted By: yooper H.V. manhole grounding - 10/16/02 07:16 PM
Several circuits of 12470, running thru manholes, deadbreak elbows in junctions, metal ladder , metal cable supports,
Ground bar, two ground rods, all grounds and shields tied together.Sound Ok???
Posted By: electric-ed Re: H.V. manhole grounding - 10/16/02 08:57 PM
Sounds like the kind of installation that should be engineered.
I would follow the specs and drawings.

Ed
Posted By: Bjarney Re: H.V. manhole grounding - 10/16/02 09:45 PM
Omission of an {often} bare-copper conductor in the same raceway with the phase cables may accelerate damage {in fault situations} to the tape/drain-wire shield under the MV-cable jacket. The additional grounding conductor is routine, well-considered boilerplate for many.



[This message has been edited by Bjarney (edited 10-17-2002).]
Posted By: yooper Re: H.V. manhole grounding - 10/17/02 01:08 PM
Guys
Theres two 500mcm in the concrete of the duct bank to each manhole and tied to the groundinging bar in each manhole. As far as designing eng. We;re it.
Posted By: Bjarney Re: H.V. manhole grounding - 10/17/02 07:56 PM
Yoop—

Sounds like you've covered it thoroughly. Is someone complaining about a “deficiency”?
Posted By: Bjarney Re: H.V. manhole grounding - 10/17/02 09:41 PM
Someone may be sniveling about expecting to see “IEEE std 837”-grade connections, but that's not an NEC or NESC requirement. [If it's specified in contract documents, that's a whole 'nother matter.]