hi, this is a double barrell question.
1.)can you feed the required outlet for HVAC maint from the same circuit that feeds a bedroom? The circuit is arc fault protected.
2.) can you feed the light in the bathroom and the light in the laundry room from the bathroom circuit? I know the laundry circuit itself can only have a built in appliance like an iron on it...nothing else and has loading restrictions..80% i think...
vent/light combo only no heat.
thanks for any replies
frodo
|
|
|
|
Joined: Jan 2002
Posts: 1,457
Member
|
Frodo, For the bathroom recept you must feed it with a 20 amp circuit. This can feed all the bath gfis,or just one bath gfi, or one bath gfi and other lights or such in that same bath only.
|
|
|
|
Joined: May 2001
Posts: 129
OP
Member
|
hi, i was reading the code and its says that a receptacle must be located in the bathroom but i didnt read anything that says you cant attach any other outlets?
thanks
frodo
|
|
|
|
Joined: Nov 2000
Posts: 2,236 Likes: 1
Member
|
210-11(c))(3)
Read closely the last sentence and the exception.
Such circuits shall have no other outlets.
Ex. Where a 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with section 210-23(a).
-Virgil Residential/Commercial Inspector 5 Star Inspections Member IAEI
|
|
|
|
Joined: May 2001
Posts: 129
OP
Member
|
hi, you guys are fast...i found the article and couldnt make it back to the comp before i got nailed...my memory is getting very bad...
got it..
thanks
frodo
|
|
|
|
Joined: Jun 2001
Posts: 196
Member
|
hi frodo, the answer to the 1st question is that there isnt anything that requires an hvac servicing receptacle from being on a specific circuit and nothing that limits an afci circuit to a bedroom, if that was the question
|
|
|
Posts: 421