A new inspector is giving me a hard time about not running a ground in my E.M.T. Can anyone steer me in the direction in which to cite code reference that E.M.T. can be used in lieu of a grounding conductor?
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
Tom Offline
Is this guy a mine inspector?
Tom
Few things are harder to put up with than the annoyance of a good example.
See Section 250-118 in the 1999 NEC, and Section 250-91(b) in the 1996 NEC.
However, I always recommend that the EGC be installed. I have many pictures of the wiring method you describe, and other metal raceways that have come apart because of many reasons that are typical -- and we all know what they are.