Posted By: C.Urch Need help with code reference - 09/19/01 09:09 PM
A new inspector is giving me a hard time about not running a ground in my E.M.T. Can anyone steer me in the direction in which to cite code reference that E.M.T. can be used in lieu of a grounding conductor?
Posted By: Tom Re: Need help with code reference - 09/19/01 09:56 PM
250-118(4)

Is this guy a mine inspector?

Tom
Posted By: Joe Tedesco Re: Need help with code reference - 09/19/01 10:00 PM
See Section 250-118 in the 1999 NEC, and Section 250-91(b) in the 1996 NEC.

However, I always recommend that the EGC be installed. I have many pictures of the wiring method you describe, and other metal raceways that have come apart because of many reasons that are typical -- and we all know what they are.