I would like to install a simple service in GRC pipe. Can i install the GEC from the meter in this pipe to gain entry into the dwelling? got code?
|
|
|
|
Joined: Feb 2001
Posts: 62
Member
|
Yes. You can install the GEC in the same conduit as the service entrance conductors. See article 230-7, exception No. 1.
|
|
|
|
Joined: Oct 2000
Posts: 5,392
OP
Member
|
Thanks Mike, do you feel there are conflictions in 250 ? i am interested in point of view here, (for those posters that see my repetitive grounding inquires)
|
|
|
|
Joined: Jan 2001
Posts: 75
Member
|
Be sure to abide by 250-64(e) for each metal enclosure that the GEC passes through.
Glenn
|
|
|
|
Joined: Jan 2001
Posts: 1,044
Member
|
Sparky,
I'll give you one of the violations that I cite in a service of this nature. I save this one for the folks who give me a hard time about correcting other violations of a serious nature. See 310-3, which requires conductors #8 & larger to be stranded if installed in raceways.
Tom
Few things are harder to put up with than the annoyance of a good example.
|
|
|
|
Joined: Oct 2000
Posts: 5,392
OP
Member
|
hmmmm, i'm tying to think of the last time i saw or used larger solid wire! I'd have to agree with that code Tom, it's a bear to put in pipe, at least of any length. anyways, the GEC discussions always seem to incite the 'lightning' angle. Do you guys see any related problems here?
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
Tom, Look at the exception to 310-3 and then look at 250-62. The exception says "as permitted or required elsewhere in this code". 250-62 permits the GEC to be a soild conductor without a size restriction. Don(resqcapt19)
Don(resqcapt19)
|
|
|
|
Joined: Oct 2000
Posts: 5,392
OP
Member
|
ok, let's go there! Let's install a 200A simple meter, GRC down JB in thru sill plate, beat a #4 cu solid thru it( just to be difficult) bonding bushings at both pipe ends. GEC enters panel , has to bond at the pipe end entering, make to the term strip the MBJ is at, then exit the panel ( not sure how to bond there?) and down to G-rods, onto h20 pipe. i'm thinking this may be nec compliant,yet electrically flawed in the nec's intent for a GEC
|
|
|
|
Joined: Jan 2001
Posts: 1,044
Member
|
Don,
You're absolutely correct. I'll have to delete this one from my list.
Tom
Few things are harder to put up with than the annoyance of a good example.
|
|
|
|
Joined: Apr 2001
Posts: 6
Junior Member
|
sparky, why do you want to do it the hard way? you only need to bond the grc at one end. either at the meter socket or main panelboard. then #6 to the rod and #4 to the water pipe from the panelboard. our utility here does not the gec in the meter socket.
|
|
|
Posts: 240