I've got a situation in which I need to use a J-box to extend an existing run. Unfortunately, the box will be placed in a location where, for aesthetic reasons, I'd prefer not to install an access panel. I thought I could install a light to circumvent this problem, but the boxes that come with small recessed halogen fixtures (my preference in this case) are too small to accommodate 3 12/2 conductors (power in, 1 beginning of the run switch, power out). Would it be code to install a j-box on the joist next to fixture such that access to the box is via the fixture hole in the drywall ceiling?
Thanks!
-TRS
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
it has been done, i think it is called a "floater". there was another B"s thread that addressed the older wirings temp rating by doing just that. the term "accessible" has 3 definitions; -as applied to wiring methods -as applied to equipment -readily accessible all evoke much debate, with given situations. we need a few more points of view here
|
|
|
|
Joined: Feb 2001
Posts: 308
Member
|
I would say it is accessible. The alternative is to have contractors who install old wires in fixtures rated 90 deg. and blow the UL listing. Is the can at least a five inch diameter?
|
|
|
|
Joined: Mar 2001
Posts: 9
OP
Junior Member
|
The can is at least 5" (I'm not sure of exact specs) and I have the option of mounting it as a remodel unit (after the drywall is up) so that it can be removed at any time.
Thanks.
-TRS
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
TRS,
The fixtures with the mounting bars on them will usually come out too after loosening several screws inside the can. Many will say that a 'floating box' that can be pulled down out of the ceiling through the hole will be acceptable. It would be best if you can relocate the splice to a more accessible area if possible.
Bill
Bill
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
the thing is, you have to know it's there, or it'll drive you nuts trying to find it
|
|
|
|
Joined: Jan 2001
Posts: 1,044
Member
|
In my opinion, the floating junction box would be a violation of 370-23. I don't see anything in this article that would allow the box to be supported by cable. This is the same article that bans homemade extension cords that use (un)handy boxes or 4x4 boxes or just about any other common box with a receptacle installed in them.
Before the days of the inexpensive circuit tracer, a customer paid me about $200 to find a loose connection in one of these boxes. I admit I'm slow on the uptake sometimes, but it took awhile for me to understand that someone would perpetrate such a dastardly deed.
Tom
Few things are harder to put up with than the annoyance of a good example.
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
well ok Tom, i have to admit, chasing down buried J-boxes does bring such langauge to mind
|
|
|
|
Joined: Jan 2001
Posts: 1,044
Member
|
Sparky,
Bad language and a whole lot more. It is enough to make you wish you were born with x-ray eyes when you're working on one of these.
Tom
Few things are harder to put up with than the annoyance of a good example.
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
Tom,
I don't recommend this as I think it is questionable also. In a previous discussion, at another BB I was asking about preferred ways of dealing with New Ceiling fixtures and older wiring types. (I think Sparky may have seen it too) I was told by several Inspectors that it was acceptable to use a 'Floater' Box to splice a short length of newer 90C wire and push it up in the ceiling. I don't see this as being much different, except that it may be easier to avoid and if it is not wiring associated with the fixture it could be a real pain to find.
Bill
Bill
|
|
|