#67155 06/27/06 09:01 PM
We installed wireing for a pool the other week. Everything passed but how exactley is a non-double insulated pool pump motor bonded. I know its a # 8 Bare but what is the exact procedure. The more I read the code book the more confused I get. Any and all help would be greatley appreciated. If you dont have enough room in this forum please e-mail me at anna729@comcast.net I live in massachuttes. Wish school was still open. My boss isnt even sure of the answer. HELP
#67156 06/27/06 09:09 PM
Steve:
Short & sweet, lug on motor to pool frame.
IF any other pool equipment, continue #8 accordingly. Anything within zone over 4Sq in. has to be bonded.
IG pool is rebar, niche shell, cups, filter, heater etc.
Basically, if in doubt, bond it.
Do not go to a grd rod, panel, sub-panel, EGC etc.
NOTE: Be very careful if it's inground in areas that adopted 2005 regarding bonding around perimeter decking. I don't have Article handy now, but read!
#67157 06/27/06 09:21 PM
If above ground every stantion must be bonded, holes in stantions must be drilled and taped and the lug must be suitable for direct burial. the #8 min must be connected @ every stantion then go to the pump motor with no break.
#67158 06/27/06 11:12 PM
Peter, is that a metal pool with significant metal to metal contact between members? If so I say it goes beyond 680.26
With that thinking we would be looping our screen cages with #8.
