I lurk on a bunch of message boards, but this one kind of blew my mind. From the HVAC-Talk board, on the wall of shame, this thread shows pics of a panel where a CB would not shut off, so the Hvac guy pulled the breaker.
QUOTE "The breaker would not turn off so I said well then I will just pull it from the panel and you see what happened."
If I am seeing this right, it appears that he pulled the CB under load, and it came apart on him. If this is true, I would think he is lucky to still be around to tell the tale.
Oh yeah, and I think it is a bit odd that I am seeing white wires attatched to breakers. Those are single pole CB's right?
Robert
#67041 06/25/06 07:33 AM
Hey Bob,
Some of the worst wiring practices I have seen has come from "Tin Benders". Saw one the other day, couldn't find the breaker for an outdoor condensing unit until I pulled the panel cover off and found two # 10s stuck up under the load side of the main.
You know the saying "The trouble with electricity is that it almost always works!"
Steve
#67042 06/25/06 11:59 AM
Looks like Zinsco breakers to me!
#67043 06/25/06 02:41 PM
That's (in slightly different words) my signature at the OHW board ( www.oldhouseweb.com )... they occasionally have nice hacks there too.