Okay i work in a health care facility in southern california. My question to all of you is are we required by law to test our receptacles in patient care areas? And if so is it all the hospital or just patient rooms...I ve looked it up on the internet but all i found was old stuff....PLEASE HELP
#66494 06/05/06 07:03 PM
Drgnz23, yes you are. You are also required to do equipotential and leakage testing. This can be found in Chapter 4 of the 2002 NFPA 99 or chapter 3 of the earlier cycles of NFPA 99.
I'll post the actual sections tomorrow.
Roger
#66495 06/05/06 07:03 PM
I think NFPA 99 requires it, I don't know if you have to follow it.
You can find more info in these links, keeping in mind they are trying to sell their product.
http://www.leviton.com/sections/prodinfo/receptic/sheets/tensiontester.htm
http://www.leviton.com/pdfs/tensiontest2.pdf
#66496 06/05/06 07:05 PM
Bob, that one was close. [Linked Image]
Roger
#66497 06/05/06 07:16 PM
Yes it was. [Linked Image]
While I was typing I was thinking that you would know the answer.
Glad I matched you. [Linked Image]
#66498 06/05/06 11:55 PM
drgnz23 Offline OP
Thank you guys...
#66499 06/07/06 11:22 AM
Drgnz23, the actual chapter sections from the 2002 NFPA 99 is, 4.3.3 through 4.3.4.2.2. (4.3.4.1.1 through 4.3.4.4.2 covers receptacle testing)