#63812 03/28/06 01:02 AM
Joined: Aug 2005
Posts: 214
E
Member
Everything also depends on the loads attached to the receptacle, in a house there will almost never be anything plugged in that would seriously strain a device, the obvious esceptions being airconditioners and space heaters. and if you work remodling houses you become very grateful for not having to jam a wirenut and extra wire into a box along with the old, stiff, rubber and cloth covered wire. Personally I think that the conection to the device is far, far more likely to fail then the device itself under load, especially if not properly installed.
I'd also like to say that back stabs may be a good thing for speed-freak tract home electricians, they do everything fast as possible, and if they had only screw terminals to hook to I can see such things as sticking unlooped wires under screws, not tightening screws down all the way etc.
-Will

#63813 03/28/06 03:32 AM
Joined: May 2004
Posts: 116
S
Member
renosteinke -

"Another assumption these days is that you'll be using a "greenie" to join the grounds together."

Ok, I'll show my ignorance, what is a "greenie" (and does it go by any other names)?

Steve


Thanks
Steve
#63814 03/28/06 04:56 AM
Joined: May 2003
Posts: 1,158
Member

#63815 03/28/06 11:23 AM
Joined: Jan 2005
Posts: 5,445
Likes: 3
Cat Servant
Member
A "greenie" is a green wire nut, made by Ideal, that has a hole in the end. To use it, you trim all your grounds back (except one). You slip the long wire through the nut, out the hole, and several inches later, tighten the nut on the remaining grounds. This gives you a pigtail for attaching to a screw.

#63816 03/28/06 11:28 AM
Joined: Jul 2002
Posts: 717
M
Member
I prefer the buchannon or stak-on barrel crimps for ground connections. They use less space, and if installed properly make a good connection. Note the words installed properly.

#63817 03/28/06 02:18 PM
Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
They also make a greenie with an attached green insulated stranded 12ga pigtail that has a spade connector on it.
I am not sure how the money works out but they are great for retro work where the EGCs are too short to reach the device. I would think that would be good in those packed fan boxes on AFCIs too where an errant ground hitting the neutral can trip the AFCI.


Greg Fretwell
#63818 03/28/06 10:53 PM
Joined: Apr 2001
Posts: 109
N
Member
Hello from South Dakota!!!!!

Forgive me for this, but I always thought that you had to pig-tail every device. I was always told that you could not rely on a device for circuit integrity, but then again I have never questioned that in 16 years.

Am I wrong?

Jon


Jon Niemeyer
#63819 03/29/06 05:53 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Jon the NEC only requires the grounding conductor and the grounded conductor of a multiwire branch circuit to be pigtailed.

(Actually they do not require a pigtail but that is the result of what they do require)

Outside of those conductors you may use the device to feed through.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#63820 03/29/06 10:45 AM
Joined: Jan 2005
Posts: 5,445
Likes: 3
Cat Servant
Member
Pigtailing is one of the more common ways that "trade practice" exceeds code requirements.

[This message has been edited by renosteinke (edited 03-29-2006).]

#63821 03/29/06 08:17 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Does it really exceed code requirements or is it simply acceptable?