#58055 10/27/05 06:35 PM
Joined: Jul 2002
Posts: 17
Q
qopanel Offline OP
Member
Approx a year ago we did a build-out for a dentist. He has been constantly blowing bulbs in can lights and just recently brought it to our attention. A voltage check was done and found about 128.9v. We have since supplied him with 130v bulbs, hoping this will solve the problem. Last night we received a call telling us his compressor motor burned out. A voltage check phase to phase showed 249.8v. The tag on the motor rates the voltage to be 208-230v and around 8amps (i forgot what it said exactly). A tech from the compressor cormpany (who first found the problem) told the dentist that the voltage is way to high. What I'm asking is, is there a plug in type conditioner that I can use instead of a buck boost? The plug configuation is a 250v 20amp.

Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
You should check with the utility and see if They can lower the voltage. That voltage should be within a specific range. Some locations it 10% and others it's 6% of 120 volts. The 130 volts seems high however the 249 volts is within range.

Joined: Jul 2002
Posts: 17
Q
qopanel Offline OP
Member
The utility is within there limits. 10% either way. This office is the 8th down the line from the main service which has is a multi metering service. It is approx 190' feet from the meter. From the main service to this office we are losing only 1v. Utility said they will do nothing.

Joined: Sep 2003
Posts: 650
W
Member
Given that the motor is burnt out, perhaps the place to look is at the motor itself.

Use a 240V motor, or get the present motor rewound to match the supply voltage.

-Jon