I'm having trouble finding the article that discusses the maximum distance allowed for conduit between boxes. Thanks.
Jesus may have been a capenter,but God was an electrician.Genesis1:3
|
|
|
|
Joined: Jun 2005
Posts: 821
Member
|
Well, what kind of conduit?
Chapter 3 of your code book covers all kinds of conduit.
|
|
|
|
Joined: Sep 2004
Posts: 174
OP
Member
|
I was always told that you can't have more than 100 feet between boxes, but I can't find it in the code book.
Jesus may have been a capenter,but God was an electrician.Genesis1:3
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
How long is your fish tape?
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: Apr 2001
Posts: 449
Member
|
The maximum length of conduit between boxes is the circumference of the earth. More than that and you will have over 360º of bends in your run. But seriously, it's not restricted by distance, it is restricted to 360º degrees of bends between pull points. I have pulled wire through 700'runs of conduit using a Mightymouse.
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
Larry Fine Fine Electric Co. fineelectricco.com
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
The only other restirction, is the pulling force and sidewall pressure that will result when the conductors are pulled into the raceway. If this is a long pull with large conductors, then you need to do a pulling calculation to make sure that the conductors won't be dammage when pulled into the raceway. Don
Don(resqcapt19)
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
Saw an artical in EC&M a while back that had calculations and formulas for pulling. Side wall and drag resistance, ect. thought I saved it, but.... lost somewhere in this box next to me.... I'll have to admit, I never learned them, and have gone on experiance for this type of thing, and over-build/design if at all worried.... Found it: http://ecmweb.com/mag/electric_simple_calculations_cable/index.html