#48327 02/10/05 12:04 AM
I would use a Wago for this, definately not a split bolt.
#48328 02/10/05 12:24 AM
If you go with the split-bolt you run the risk of a red tag. Split bolts are listed for 2 conductors only.
Ilsco makes a listed 3 conductor split bolt. The listing limitation of 2 wires is 2 wires of the max size for the bolt- for instance a #2 split bolt has a listed max for 2 #2 conductors. When used with smaller conductors such as #12 the amount allowed is raised.
#48329 02/10/05 08:23 AM
No. You can only install the listed wire combinations in any splicing device.
Don
#48330 02/10/05 09:09 AM
I have never seen on any of those charts show you can put more than 5 wires under a single connector. I believe method of shoving all these wires under one wire nut is poor.
Ideal #30-454
3 to 6 12 AWG
5 or 6 14 AWG
If you make the splice as Hal (hbiss) described it will be a fine splice.
This thread is a good illustration of how we each have are own methods of working and each way is 'right' for us. [Linked Image]
For myself
The 'bridge' method described by macmikeman would be a last resort for me.
I would need a gun to my head to use a Wago as described by Electric Eagle.
A split bolt for 6 or 8 conductors, not a chance.
To each their own as long as it meets code. [Linked Image]
Bob
#48331 02/10/05 10:30 AM
The trick is not to shove the wires under the wire nut. If you can make a good splice it does not matter if you have five or six wires as long as the wirenut is rated for it.
[This message has been edited by Electricmanscott (edited 02-10-2005).]
#48332 02/10/05 01:33 PM
Try the Ideal In-sure connectors. I picked some up at Depot. Work for 2 to 8 wires I think. Here is a link.
They also have a test port.
http://www.idealindustries.com/IDEAL-EZ/products.nsf/ItemMasterLookup/p30-688?OpenDocument
Bill K
#48333 02/10/05 02:00 PM
Bill those are another kind of 'Wagos'
[Linked Image from idealindustries.com]
There are UL listed and could be used for the splice the opening post asked about.
I will not use them.
Back stab receptacles where / are UL listed also and their history of failure is high enough in my mind not to use them either.
I have a hard time believing that the small piece of spring steel that makes contact with the wire makes a connection as reliable as a properly installed wire-nut.
That is just my opinion and how I choose to work, as I said earlier to each their own. [Linked Image]
Bob
#48334 02/10/05 02:49 PM
Yep
Sorry my first response was inteded for the opening question.
Bill K
#48335 02/10/05 03:01 PM
Bill no reason to be sorry and welcome to ECN. [Linked Image]
Don't let my personal opinion(s) keep you from expressing yours.
We all have an equal say here, it is an open forum.
I may have 'Moderator' under my name but that does not mean my opinion is anymore valid then a new member.
Keep on posting. [Linked Image]
Bob
#48336 02/10/05 03:34 PM
tkb Offline
The only place I would use the Wago type connectors is in a fixture for a ballast change. Most of the sockets are push in and so are some of the ballasts. The fixture manufactures also use them to extend the wires for an 8' fixture.