1 members (Scott35), 409 guests, and 38 robots.
#42842 09/28/04 11:13 AM
400.7(A)(8) would seem to permit both the supply to and the feed from the UPS to be a flexible cord. Clearly this UPS is intended to be used with flexible cords on both the input and the output
I do not see the use of a flexible cord in this situation as a problem, as long as all of the standard flex cord precautions are met. There are UL listed generator transfer switches that use a panel mount twist-lock inlet, and which are connected to the generator via a flexible cord.
The SDS issue is also a red herring, because most UPS devices are not galvanically isolated input to output, and are thus more like auto-transformers. Both ground and neutral continuity are maintained through the devices, and thus they are not SDSs.
-Jon
#42843 09/28/04 01:35 PM
Tom Offline
I don't believe that a UPS is an appliance, other than built in losses, it does not consume power and it certainly doesn't wash my clothes or fry my food [Linked Image] .
Flexible cord is not a Chapter 3 wiring method and cannot be inserted into a branch circuit. Check out definitions of "branch circuit " and "appliance."
#42844 09/28/04 08:26 PM
UPS installation can be complicated. To start with, the UPS is only PART of the system; just as inportant is the transfer switch.
OK, so your UPS needs to be addad to the circuit. Yours sounds small enough to easily fit into a pull box, and be hard-wired.
Larger units, which often have wheels, are commonly attached with SO cord. These cords are connected to the panel with strain-relief connectors, and hard-wired to the circuit.
For other applications -such as a means to attach a power cord to a trailer, the device used is called a "power inlet." It's kind of like a cover plate with a plug mounted in a recessed area. This allows you to push a cord cap onto it. The problem with a UPS is that these prongs will be 'hot' as long as the batteries have a charge.
The first thing to do is contact the UPS manufacturer, and find out what his reccomendations are.
