Safety at heights?
0 members (), 504 guests, and 20 robots.
#42769 09/25/04 06:36 PM
jayson Offline OP
what size of wire is service wire is needed for a 200 amp panel copper size? aluminum size?
#42770 09/25/04 06:39 PM
The smallest permitted would be 4/0 AL for a dwelling service
#42771 09/25/04 07:49 PM
We use 3/0 copper for all 3. Lots of locals want that. Someone elce might know the code but I think NEC lets you go one smaller?
#42772 09/25/04 07:51 PM
2/0 copper
4/0 aluminum
#42773 09/25/04 07:54 PM
If we are talking dwelling unit services the NEC allows the use of Table 310.15(B)(6).
200 amp service 2/0 CU or 4/0 AL
100 amp service 4 CU or 2 AL
This does not apply to commercial services.
[This message has been edited by iwire (edited 09-25-2004).]
#42774 09/26/04 11:07 AM
jayson Offline OP
thanks guys