question; an office building has a total area of 50,000 sf, the actual number of gen-purpose receptacle outlets is unknown and the connected load equals the calculated load. how many 120 volt,2-wire,20 amp branch circuits are for the lighting and receptacles ? I missed this one on a practice exam. the options were,21,92,112,or 118. can someone could show me the calculations,.... thanks
How about 92...
50,000 sq. ft. X 3.5 VA (from Table 220.3A)=175,000 VA required. 175,000/1920 (16 amps continuous X 120 Volt)= 91.145
What did you get?
[This message has been edited by Redsy (edited 06-19-2003).]
thanks,redsy, I fogot to change the 20amp ckt to 1920 va.
do you have an example on using table:220.34 for selecting feeder/service conductors for a school, there are no examples for this in the nec handbook ?
Look at Table 220-3(a), if you look at the table for office buildings it gives you a value of 3.5 v/a per sq. foot BUT there is a footnote 'b'...if you read this footnote it indicates you must ADD an additional 1 v/a per sq. ft. for general-purpose receptacle outlets where the actual number of receptacle outlets is UNKNOWN. Therefore you have a total v/a per sq. ft. of 4.5 calculated as follows: 3.5 v/a x 50,000 sf. = 175,000 va x 125% (lighting is considered a continuous load) = 218,750 v/a + 50,000 v/a (1 v/a per sf for unknown receps) = 268,750 va/120v = 2239.58A /20A ckt rating = 112 circuits Go to RKeiss' website ( www.elec-toobox.com), in his 'Code Quiz' section, May, 2001, quiz question #6 - he takes you through the steps of computing the answer for the same situation you asked. [This message has been edited by dana1028 (edited 06-19-2003).]
Good catch, dana. But, I don't understand why the 125% is only added to the basic 3.5 va/sq.ft. and not the additional 1 va/sq.ft.
I still would suggest the following...
50,000 x 4.5 = 225000 225,000 / 1920(80% of 120x20) = 117.19 (118 ckts.) OR... 50,000 x 4.5 x 125% = 281,250 281,250 / 2400 (120x 20) = 117.19 (118 ckts.)
because they are applying the 1 va to the recep load and applying the 3-1/2 va to the lighting load...lighting loads are considered continuous loads in non-dwelling occupancies....if you read the title to the table " General Lighting Loads"
...per your calculations - 117.19 is rounded down, not up (see 220-2b)...117 is not one of the options for an answer.
[This message has been edited by dana1028 (edited 06-20-2003).]
Thanks for the clarification, dana.