Safety at heights?
1 members (Scott35), 561 guests, and 44 robots.
#24677 04/18/03 08:59 PM
Z
Zapped Offline OP
I have a client (commercial) that wants me to put outlets on a countertop, facing up. I've tried to convince him with common sense that this is a bad idea (spills, etc...) even when GFCI protected, but an NEC reference would be helpful, as he's being pretty persistant. Can anybody guide me to a specific code that would find this in violation?
I'll appreciate any input, thanks
-SC
#24678 04/18/03 09:35 PM
Zapped:
It is definetly a NEC violation to install receptacle outlets in a "face-up" manner.
I don't have the bible handy to give you the article at the moment
#24679 04/18/03 10:02 PM
406.4(E)
#24680 04/20/03 07:18 PM
Z
Zapped Offline OP
Thank you gentlemen!!
#24681 04/20/03 08:50 PM
406.4(E) only applies to dwelling units. Since this is a commercial kitchen I'm not sure it would be a violation to install the receptacles this way but I think we all would agree its not a good idea.
Curt
Curt Swartz