Regarding clamps for non-metallic cable, what do the "N" and "T" mean?
[Linked Image from 65.108.216.53]
The N stands for Non-metallic Cable
The T stands for "tubing" and is a reference to Loom tubing.
These clamps are listed for both NM cable and Loom.
Hence the name "Loom Clamps"...
-Virgil
5 Star Inspections
Member IAEI
T stands for tube or loam(???), are those holes big enough to get two K and T wires in one hole with the tube.
As you know you cannot separate the wires ie one per hole because of inductive heating.
just my 2 cents.
WOC
K&T wiring normally is separated throughout the system and it enters boxes via 2 separate holes. I'm not sure that there is enough separation of the wires in small wall cases to cause inductive heating problems, which is also of course related to the amount of current flowing.
Could you elaborate on this? I don't understand. How can separating wires cause heating?
I thought you had to derate when you bunched up wires because that is when they can potentially start heating up. [Linked Image]
Sven,
That's a good Tech Area question.
You are suppose to cut the notch out between the two holes in order to reduce the magnetic build up between the 2-K&T wires. This way each K&T wire enter the box through it's own space.
Thanks for the replies.
...The things one can learn on this board!!!!
Sven,
Look at 300.20