My question is I have a 250 gallon Water heater do I calculate at 100% or 125%? This is branch circuit not feeder calculations. Thanks
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
That's a big tank.
Is this for a locker room with showers?
Ghost307
OK I see article 422.10 says 125% but where is the code reference to the breaker size one size higher? My water heater is listed at 87 A so 90 A is next standard breaker size.
You need to take 125% of the full load current; so it needs to be treated as a 108.75A load.
Make sure to also upsize the wire accordingly.
Ghost307
Thanks, ghost.
H20
Yeah exactly gym inside google bldg.