Safety at heights?
0 members (), 516 guests, and 17 robots.
#217072 04/22/16 09:42 PM
brsele Offline OP
So Ontario is adopting the new code starting May 1st.
As I believe most of you have been working with the new code for a year now, I have a question with regards to the new table 39.
As per 8-104(6)(a), when would somebody put an 89A calculated load on a 100A service?
Or is somebody manufacturing main breakers now rated for 100%
Thanks... Bruce
brsele #217073 04/23/16 05:35 PM
twh Offline
8-200(3) says calculated loads for residential services are not continuous.
brsele #217074 04/23/16 09:03 PM
brsele Offline OP
Thanks TWH.
This question came to me as I've been asked to wire a new house being built with electric heat. A 100A service was specified.
This is the first time in my life I've been asked to supply a 100A service for a new house and electric baseboard heaters.
So I did a load calculation and came up with 85A.
I always thought that the max. calculated load for a 100A service was 80A and the max. for 200A was 160A.
I'm wondering if this is a case where I was originally taught wrong and never questioned it, or if something changed and I never noticed because everybody asks for a 200A service.