#216940 - 03/16/16 08:40 AM Confusion with 250.90 (2011)
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
250.92(B) says bonding jumpers....shall be used around impaired connections..... and in the same paragraph goes on to say that standard lock nuts or bushings shall not be the only means for the bonding required by this section. I thought the second sentence referred back to the first sentence where jumpers are required around impaired connections. An associate says no, the second sentence refers to all connections on the utility side of the service whether impaired or not.

Further confusion arises in 250.92(B)(3) where it allows threadless connectors made up wrench tight. What is the difference if a threadless connector is used with a standard lock nut versus a threaded piece of RMC using standard lock nuts?


Edited by BigB (03/16/16 08:41 AM)
Top
2017 / 2014 NEC & Related Books and Study Guides
#216944 - 03/18/16 07:41 AM Re: Confusion with 250.90 (2011) [Re: BigB]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
BigB:

Utility requirements may be 'above and beyond' NEC rules.
_________________________
John
Top
#216951 - 03/18/16 09:00 PM Re: Confusion with 250.90 (2011) [Re: HotLine1]
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
Originally Posted By HotLine1
BigB:

Utility requirements may be 'above and beyond' NEC rules.


Not our POCO. The only thing they are concerned with is their ability to access the meter for non-payment lockout and that their side is locked and sealed.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 96 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals